Skip to main content
Energy & carbon

TM44 Air Conditioning Inspections Explained

TM44 air conditioning inspections are a legal requirement for larger AC systems. This guide explains which systems are in scope, who the duty falls on, the deadlines that catch people out, what enforcement actually looks like, and how the rules differ across the UK. Every figure below is referenced to the regulation it comes from.

Diagram summarising TM44 air conditioning inspection for facilities and estates teams, covering Which systems need a TM44 inspection and Who the duty actually falls on

In short

A TM44 inspection is a statutory energy assessment of air conditioning systems with an effective rated output over 12kW, required under the Energy Performance of Buildings Regulations. Carried out at least every five years by an accredited assessor, it reviews the system's efficiency and recommends improvements.

Which systems need a TM44 inspection

In England and Wales the duty comes from Part 4 of the Energy Performance of Buildings (England and Wales) Regulations 2012, which applies to "air-conditioning systems with an effective rated output of more than 12kW" (regulation 17(1)). Note the wording: more than 12kW, so a system rated at exactly 12kW is outside the England and Wales regime.

The part most often misread is how units are added together. Regulation 17(2) does not ask whether units share a refrigerant circuit, a manufacturer or a control panel. It says that where the relevant person "has the power to control the temperature of more than one individual air-conditioning unit in a building", each unit is treated as a component of a single system. The test is the extent of one person's control over the building, not how the plant is plumbed. Ten unconnected 2kW split units in one office, all under the control of the same facilities manager, are a single 20kW system and in scope — a conclusion the government's own guidance states directly, confirming that scope "will include systems consisting of individual units which are less than 12kW, but whose combined effective rated output is more than 12kW".

Effective rated output has a defined meaning, and it is not the figure most people reach for. Regulation 17(3) defines it as "the maximum calorific output specified and guaranteed by the manufacturer of the system as being deliverable during continuous operation while complying with the useful efficiency indicated by the manufacturer" — a manufacturer's rating, not a measured duty, an electrical load, or a figure worked back from the building's cooling demand.

One further limit is easy to miss: since 2015 the duty in regulation 18(1) has applied to the "accessible parts" of the system. An assessor is not required to open up sealed plant or gain access to units that cannot reasonably be reached. That narrows the inspection, but it does not narrow the scope — an inaccessible unit still counts towards the 12kW threshold.

  • More than 12kW effective rated output, assessed across the system (reg 17(1))
  • Units aggregate where one person can control the temperature of more than one of them in a building (reg 17(2))
  • Effective rated output is the manufacturer's guaranteed continuous output, not a measured duty (reg 17(3))
  • The inspection covers the accessible parts of the system (reg 18(1))

Who the duty actually falls on

The duty sits on "the relevant person", and the government's guidance draws the line more sharply than most summaries of it do: the person who controls the operation of the system is the person who controls its technical functioning, "not someone who does no more than adjust the temperature". A tenant with a wall controller is not the duty holder. A managing agent or in-house team that decides how the plant runs, when it runs and who maintains it, is.

That has a practical consequence worth knowing before an enforcement officer explains it: where a central air conditioning system is under the control of the building owner or manager, the guidance states that occupiers of the building would not be liable for a penalty charge for any breach of the duties. In a multi-let building the exposure normally sits with the landlord or its agent, not the tenants — which is also why the obligation tends to be invisible until a lease compliance schedule or a due diligence questionnaire asks for the report.

The duty is not delegable by contract. A maintenance contractor can carry out the work and an assessor can perform the inspection, but the regulations place the duty on the relevant person, and it is the relevant person who receives the penalty charge notice.

The five-year cycle, and the three-month rule nobody mentions

Regulation 18(1) requires inspection "at regular intervals not exceeding five years". There is no grace period built into that wording: the interval is a maximum, so a report that has passed its fifth anniversary is a breach from that day, not from the day someone notices.

For a new system, regulation 18(3)(a) sets the first deadline at the end of five years beginning with the date the system was "first put into service" — commissioning, not purchase, installation or practical completion. Systems already in service before 2008 had fixed backstop dates that have long passed: 4 January 2009 for systems over 250kW, and 4 January 2011 for systems over 12kW.

The provision that catches people out is regulation 21. Where the relevant person changes and the new relevant person is not given an inspection report, they must ensure the system is inspected within three months of becoming the relevant person. Not five years — three months. This bites on every change of managing agent, every acquisition, and every in-sourcing of an FM contract where the previous holder's paperwork does not come across. The companion duty in regulation 20 is what prevents it: the relevant person must keep the most recent inspection report, and on a change must give it to the incoming relevant person. A report that is handed over resets nothing and costs nothing; a report that is lost triggers a three-month clock and a fresh fee.

  • Intervals not exceeding five years, with no grace period on expiry (reg 18(1))
  • First inspection within five years of the system being first put into service (reg 18(3)(a))
  • Keep the most recent report, and hand it to the incoming relevant person (reg 20)
  • No report handed over on a change of control: inspect within three months (reg 21)

What the inspection covers

A TM44 inspection (named after the CIBSE guidance it follows) assesses how efficiently the air conditioning is providing the building's cooling, and where energy and cost could be saved. It is an energy assessment rather than a maintenance service, but it draws on the system's condition and operation.

Regulation 19(2) fixes the minimum content: an assessment of the air-conditioning efficiency and of the sizing of the system compared to the cooling requirements of the building, together with advice on cost-effective improvement to its energy performance, on replacement of the system, and on alternative solutions. A 2020 amendment added regulation 19(2A), requiring the report to consider the system's capabilities to optimise its performance under typical operating conditions — in practice, a closer look at controls and how the plant is actually being run rather than how it was designed to run.

  • The efficiency of the installed AC equipment relative to the cooling load
  • Sizing — whether the system is appropriately matched to demand
  • Controls, and the system's capability to optimise under typical operating conditions
  • Maintenance condition as it affects efficiency
  • Advice on cost-effective improvement, replacement, and alternative solutions

What a TM44 air conditioning inspection report contains

The output is a written report, given to the relevant person as soon as practicable after the inspection and lodged on the Energy Performance of Buildings Register, from which it takes the reference number that makes it valid. Reports produced on or after 6 April 2012 must carry that reference number, and only reports produced and lodged by accredited energy assessors count. Data entered on the register is kept there for at least twenty years.

Regulation 19(3) prescribes six items the report must contain, which is why the same headings appear whoever the assessor is: the register reference number, the address of the building, the assessor's name, the name and address of the assessor's employer or trading name, the date of the inspection, and the name of the accreditation scheme the assessor belongs to.

The part that earns the fee is the recommendations, where each finding is paired with an action — clean fouled coils, correct a setpoint, replace a failed sensor, install sub-metering, consider replacing an oversized or obsolete unit. A good report also lists the documentation the assessor could not find, which is a useful audit of the O&M records in its own right. Like an EPC, the value is in acting on the findings; the report itself changes nothing.

  • Register reference number, building address and inspection date (reg 19(3))
  • Assessor's name, employer and accreditation scheme (reg 19(3))
  • Efficiency and sizing assessment against the building's cooling requirements (reg 19(2))
  • Advice on improvement, replacement and alternative solutions (reg 19(2))
  • In practice: documentation the assessor asked for and could not find

Enforcement, penalties and appeals

Enforcement in England and Wales falls to local weights and measures authorities — trading standards (regulation 34(1)). They may act on complaints or open their own investigations, and an authorised officer can require the relevant person to produce a copy of the inspection report.

The amounts are fixed in regulation 38 and are frequently misreported, including the second one. A breach of the duty to have the system inspected, to keep the report, or to hand it over on a change of relevant person carries £300 (regulation 38(1)(d), covering regulations 18(1), 20(1), 20(2) and 21). Failing to produce the report within seven days of a request carries £200 — not £300 — under regulation 38(1)(e), which covers a breach of regulation 35(5). The seven days run from the day after the requirement is imposed, and the request itself cannot be made more than six months after the last day the duty applied.

These are civil penalty charges, not criminal offences, and the distinction matters because it changes what follows. A penalty charge notice must give at least 28 days to pay or to ask for a review, and cannot be issued more than six months after the breach (or, for a continuing breach, its last day). The authority must withdraw the notice where the recipient can show they took all reasonable steps and exercised all due diligence to avoid breaching the duty. After a review, there is an appeal to the county court within 28 days, heard as a rehearing. An unpaid charge is recoverable as a debt. There is one genuine criminal offence in this Part, and it is not about the report: obstructing an enforcement officer is an offence carrying a fine of up to level 5 on the standard scale (regulation 43).

The direct financial exposure is plainly modest against the cost of the inspection, which is one reason compliance has historically been patchy. The larger exposures are commercial: a missing report surfaces in property due diligence and lease compliance schedules, and the efficiency findings themselves regularly identify running-cost savings worth more than the fee.

  • £300 for failing to inspect, keep the report, or hand it over (reg 38(1)(d))
  • £200 — not £300 — for failing to produce it within seven days (reg 38(1)(e))
  • Civil penalty charges, with at least 28 days to pay or seek a review
  • Withdrawn if the recipient shows all reasonable steps and due diligence
  • Appeal to the county court within 28 days of a confirmed notice

England and Wales, Scotland and Northern Ireland are not the same regime

The three regimes are usually described as parallel. They are not, and the differences are substantive enough to matter to anyone running an estate across borders. The government's own guidance for England and Wales says plainly that buildings in Northern Ireland and Scotland "are subject to separate regulatory requirements and are not covered by or referred to in this guidance".

Northern Ireland is the close match. The Energy Performance of Buildings (Certificates and Inspections) Regulations (Northern Ireland) 2008 apply to systems with an effective rated output of more than 12 kW (regulation 14(1)), use the same aggregation test based on the relevant person's power to control the temperature of more than one unit (regulation 14(2)), require inspection of accessible parts at intervals not exceeding five years (regulation 15(1)), and impose the same three-month duty on an incoming relevant person who is not given the most recent report (regulation 18). The penalty for breaching those duties is also £300 (regulation 35(1)(d)).

Scotland is the outlier, and reaches the same destination by a different road. The duty is not in Scotland's Energy Performance of Buildings Regulations at all — those cover certificates only. It sits in regulation 17 of the Building (Scotland) Regulations 2004, as a continuing requirement on the owners of buildings under section 2 of the Building (Scotland) Act 2003. Four differences follow. The duty is on the owner, not on whoever controls the operation of the system. The exemption is for systems with a total effective output rating of "less than 12 kW", so a system at exactly 12 kW is in scope in Scotland and out of scope in England and Wales. Systems used solely for processes within a building — the classic case being dedicated IT and server-room cooling — are expressly excluded in Scotland, an exclusion that has no counterpart in the England and Wales regulations. And enforcement runs through the building standards system rather than through trading standards penalty charge notices.

What is common across all three is the five-year maximum interval, the coverage of accessible parts, and the reliance on CIBSE TM44 as the underlying inspection methodology.

  • England and Wales: SI 2012/3118 Part 4 — more than 12kW, duty on the relevant person
  • Northern Ireland: SR 2008/170 Part 4 — materially the same regime, same £300 penalty
  • Scotland: Building (Scotland) Regulations 2004 reg 17 — duty on the owner
  • Scotland exempts systems under 12 kW and those solely serving a process
  • All three: accessible parts, intervals not exceeding five years

Why the UK threshold is 12kW when the EU's is now 70kW

The 12kW figure is not a UK invention. It is the threshold in Article 15(1) of the original Energy Performance of Buildings Directive, 2010/31/EU, which required member states to establish regular inspection of the accessible parts of air-conditioning systems "of an effective rated output of more than 12 kW". The UK regulations implemented that number directly, and it is why the same 12kW appears in all three UK regimes.

The EU subsequently moved. As amended in 2018, Article 15(1) now requires inspection of air-conditioning systems, or combined air-conditioning and ventilation systems, "with an effective rated output of over 70 kW". The UK did not follow that change, so the UK threshold remains the original 12kW while the EU's is nearly six times higher.

The practical significance is for anyone comparing a UK portfolio against a European one, or reading European guidance and assuming it transfers. It does not: a 40kW system that is comfortably outside the current EU inspection requirement is squarely inside the UK one. The direction of travel is worth noting too — the UK threshold is the more stringent of the two, not the more relaxed, which is the opposite of the assumption people usually bring to post-Brexit compliance questions.

What a TM44 inspection costs

One element of the cost is fixed in law and can be stated precisely: the fee for entering the data from which an inspection report is produced onto the register is £1.70, set by regulation 28(b) of the 2012 Regulations and last changed on 1 April 2022. That is the register fee alone, and it is a rounding error in any quotation.

The assessor's fee is the real number, and we do not publish a range for it, because we could not verify one to the standard the rest of this page is held to. TM44 inspections are almost never procured as standalone public contracts — they are bundled into wider HVAC maintenance and compliance packages, so the published award data that would let us derive real prices does not isolate them. The price guides that do quote figures are not independent of one another and none is a primary source. An invented range on a compliance page is worse than no range, so there is none here.

What can be said usefully is what moves the number, because that follows from the regulations themselves. Assessors price by the number of accessible units they must physically inspect and how spread out they are, so a VRF network of forty indoor units across four floors costs several times a single packaged rooftop unit. Because the scope is set by aggregation across everything one person controls, the unit count — not the building's floor area or its cooling load — is the driver. Good asset records, drawings and accessible plant reduce time on site; missing data plates, locked risers and ceiling-void units that need a cherry picker or an out-of-hours visit increase it. For a portfolio, inspections are usually quoted per site and the five-year cycles aligned so that one renewal date covers the estate. Get three quotes on a scoped unit schedule rather than a floor area, and they will be comparable.

  • Register lodgement fee: £1.70 per inspection report (reg 28(b), from 1 April 2022)
  • The assessor's fee is driven by the number and accessibility of units, not floor area
  • Good asset records and drawings reduce time on site; inaccessible plant increases it
  • Scope quotes on a unit schedule, not a floor area, so they can be compared

Portfolio inspections and getting ready for one

For an estate of many buildings, TM44 is usually procured as a portfolio contract so the inspection dates align and one assessor firm holds the register references. The preparation is the same whatever the scale, and it is mostly documentation: an asset list of every AC unit with location, make, model, rated output and refrigerant; the drawings or schematics showing what serves what; the F-Gas logbook, which already records refrigerant charge and leak checks and which the assessor will ask for; the maintenance records for the last five years; the previous TM44 report and what was done about it; and access arrangements for roof plant and ceiling-void units. An assessor who can work from good records spends less time on site, and the fee reflects it.

TM44 sits alongside two other regimes that touch the same plant and are easily confused with it. F-Gas leak checks are a refrigerant-containment duty carried out by a certified engineer at intervals set by the charge size, not an energy assessment. Routine planned maintenance — the checklists for chillers, VRF systems and split units — is what keeps the plant in the condition the TM44 assessor is looking for. Keeping all three sets of records retrievable in one place is what turns a five-yearly compliance chore into a straightforward one.

Free tools for this

How this applies by sector

Compliance & CAFM

Track TM44 inspections on a compliance register

PM Assist's building compliance software holds this duty on a register for every building you manage, included in every paid plan.

  • Air Conditioning Inspection (TM44) sits on the compliance register, showing when it was last done, when it is next due and the certificate behind it.
  • Duties with no record held are listed as gaps, so nothing is missed just because nobody logged it.
  • AI reads your certificates and proposes the dates and remedial actions; a person checks them against the source document before they count.

Sources

The regulatory positions on this page come from the following primary sources. Where guidance and legislation differ, the legislation governs — always confirm the requirements that apply to your own site and jurisdiction.

Frequently asked questions

How often is a TM44 inspection required?
At intervals not exceeding five years, for systems over 12kW effective rated output. Regulation 18(1) sets that as a maximum rather than a target, so there is no grace period: a report that has passed its fifth anniversary puts the relevant person in breach from that date. A new system must be inspected within five years of being first put into service.
What size of air conditioning needs a TM44 inspection?
More than 12kW effective rated output in England, Wales and Northern Ireland — and in Scotland, anything that is not below 12 kW, which means a system at exactly 12 kW is in scope there but not in England and Wales. Effective rated output is the manufacturer's guaranteed continuous output, not a measured duty. Crucially it is assessed at system level, so several smaller units can together exceed the threshold even if no single unit does.
How are separate air conditioning units added together?
Not by how they are wired or plumbed. Regulation 17(2) says that where the relevant person has the power to control the temperature of more than one individual air-conditioning unit in a building, each unit is a component of a single system. The test is the extent of one person's control, so ten unconnected 2kW split units under one facilities manager form a single 20kW system and are in scope.
Who can carry out a TM44 inspection?
An energy assessor accredited specifically for air conditioning inspections, and a report is only valid once lodged on the register by such an assessor. In Scotland the inspection must be carried out by an accredited expert belonging to a protocol organisation approved by the Scottish Government. The inspection is separate from routine maintenance, although the assessor will consider the system's maintenance condition as part of assessing its efficiency.
What is the penalty for not having a TM44 inspection report?
£300 for failing to have the system inspected, to keep the report, or to give it to an incoming relevant person, under regulation 38(1)(d). Failing to produce the report within seven days of a request from trading standards carries a separate £200, under regulation 38(1)(e) — a figure often misreported as £300. Both are civil penalty charges rather than criminal offences, with at least 28 days to pay or request a review and an appeal to the county court.
I have just taken over a building and there is no TM44 report. How long do I have?
Three months, not five years. Regulation 21 requires a new relevant person who is not given an inspection report to ensure the system is inspected within three months of taking over. This catches changes of managing agent, acquisitions and in-sourced FM contracts. The outgoing relevant person has a matching duty under regulation 20(2) to hand the report over, so ask for it during the transfer — it is the cheapest way to avoid the clock starting.
Does TM44 apply to VRF systems and split units?
Yes, where the combined effective rated output of the system exceeds 12kW. A VRF system with one outdoor unit and many indoor units is a single system for this purpose, and several split units in one building under common control are aggregated. Portable units and systems that only provide heating are outside scope. In Scotland, systems used solely for a process — dedicated server-room cooling, for example — are expressly excluded; that exclusion has no counterpart in England and Wales.
What if some units cannot be reached?
The duty in regulation 18(1) applies to the accessible parts of the system, so an assessor is not required to open sealed plant or reach units that cannot reasonably be accessed. That limits the inspection, not the scope: an inaccessible unit still counts towards the 12kW threshold. In practice, improving access before the visit is usually cheaper than the return visit or specialist access equipment it avoids.
Is a TM44 inspection the same as an F-Gas leak check?
No. An F-Gas leak check is a refrigerant-containment duty carried out by a certified engineer at intervals set by the CO₂-equivalent charge. A TM44 inspection is an energy-efficiency assessment carried out every five years by an accredited assessor. They cover the same plant but different duties, and the assessor will normally ask to see the F-Gas logbook.
Where can I find an existing TM44 report for a building?
Reports are lodged on the Energy Performance of Buildings Register and carry a reference number; data stays on the register for at least twenty years. Northern Ireland maintains its own register. If nothing is lodged, either no inspection was done or it predates mandatory lodging, and in both cases a new inspection is the practical answer. Keep a copy with the building's O&M and compliance records so it can be produced within the seven-day window.

Keep AC plant documentation at hand

PM Assist makes your air conditioning O&M data, maintenance history, and energy records searchable — supporting efficient inspections and acting on the recommendations.

  • Upload and organise building documentation
  • AI-powered search across all your manuals
  • Source-cited answers for every query
  • Team collaboration and access control
  • No credit card required to start

Knowing the standard is one thing. Finding it in the paperwork is another.

Ask an O&M manual a question and get the answer back with the page it came from. No signup, and you can drop in your own PDF instead of the sample.

“When was the last F-Gas check?”

Runs against a sample chiller manual so you can see the shape of the answer — then try it on one of yours.